Heating Installation Tip: Load Calculations

Friday, January 13th, 2012

Do you ever feel that your Kent home just doesn’t get cool enough during the warm months or warm enough during the cold months? You have tried to adjust your thermostat to the right comfort level but it just never seems right. And on top of that, you notice that your utility bills keep going up and up. Even when you dial up the thermostat in the summer and dial it down in the winter to saving on energy usage, your bills are still about the same.

You could try adding fans and shedding clothes during the warm months or wearing sweaters and crawling under a pile of blankets in the cold months. But do you really enjoy living that way? There must be another solution as to why your heating and cooling (HVAC) system is just not keeping you comfortable – and affordable.

That air conditioning condensing unit sitting in your backyard and the furnace in your basement should be making your home as comfortable as possible. But in many cases, they are not. That’s because whoever installed those HVAC system components didn’t do their homework on your home. The components were sized incorrectly. If a furnace or air conditioner is sized incorrectly, it usually cannot keep up with the demand for heat or cold and often puts such a burden on the equipment. As a result, regular failures and repair bills are commonplace.

And it may not be the fault of the installing HVAC contractor. Over the years your home may have undergone renovations including additions and new windows, which have increased the square footage or demand for more heating or cooling. Those renovations may not have included upgrades to your home’s HVAC system.

So how do you check for the right size? Call a Kent HVAC contractor and ask for an energy audit for your home. The audit will include several key checks including a load calculation, which adds in the size of your home’s living space, number of door and windows where heat loss or gain could occur, and a check of heat loss or gain through leakage in cracks, roofs, crawlspaces, etc. An energy audit will determine what size of furnace or air conditioner is needed to meet the heating or cooling needs of your home and its own individual characteristics. Your HVAC contractor may also factor in the number of building occupants and normal usage patterns, i.e. having a home office or stay-at-home parent versus a working family where your home is occupied mostly at nights or on weekends.

All of these factors are considered when determining the equipment size. In air conditioning jargon, you will hear about tonnage of cooling capacity. An example may be a 2.5 ton air conditioning unit for a 2,000 square foot home. In furnace jargon, you will learn about Btu ratings, which are British thermal units. Most furnaces are sized in 20-25,000 Btu increments. Each is matched to the cooling or heating needs of your home. Your HVAC contractor will likely recommend using a programmable thermostat, too. That way, you can set the temperature of one or more zones in your home to when each zone is occupied.

Make sure you don’t hire someone who “guesstimates” how much cooling or heating capacity you need for your home. Find a qualified professional who will make the correct calculations and who will qualify their recommendations. A properly sized HVAC system will equate to manageable utility bills and above average indoor comfort. You can live with that.

Continue Reading

Is Your Kent Home More Valuable with Energy Efficient Appliances?

Monday, November 28th, 2011

It’s impressive the things people do to improve the value of their Kent home. We’re talking about crown molding, new floors, new siding, upgrades to the landscaping and much more. The cost of upgrading these things can grow out of hand quickly and if the boost to your home’s value isn’t equally exponential, it’s hard to justify the expense.

So, it’s always nice to find a simple upgrade that can be performed for a few hundred dollars that will save you money immediately and improve the value of your home in the future. Your appliances are one such upgrade.

The Value of Energy Efficiency

An energy efficient washing machine can save upwards of $150 per year on water costs. An energy efficient toilet cuts consumption by as much as 150%. Low flow shower heads cut water costs by one third to one half and your heating and air conditioning systems can be improved by 10-35% depending on the upgrades available to you.

When you add up all those savings, the result is a tremendous amount of money that can be saved each year on everything from your water bill to your cooling needs. Imagine what happens when someone looks to buy your home. They see that there are all new appliances with energy efficient ratings that will save them money.

It’s not just lower bills; it’s a decrease in upfront investment. On the surface, it’s unlikely that your energy efficient appliances will directly increase the value of your home, but they can increase the likelihood of someone paying what you’re asking for the home. They add value to the livability of the home, if not the property itself and in today’s housing market, that’s a major plus.

Best Upgrades

The best upgrades to your home’s appliances are the ones that save money without additional work. Water saving appliances should top your list since they are used throughout the year. A new toilet, a new washing machine, a new shower head and sink faucets all designed to cut down on water use are valuable upgrades. Major upgrades to your heating and cooling are good if you need an upgrade anyway or you plan on staying in your home for a few years.

Continue Reading

Get the Best Value From Your Contractor in Tukwila

Wednesday, October 5th, 2011

When looking for the best value from a Tukwila service provider, it is best to understand what value means to you. The dictionary defines value as “a fair return or equivalent in goods, services, or money for something exchanged.”

In the case of a mechanical contractor, customers are looking for value in the quality of the replacement or newly installed parts or equipment. For example, if your contractor gives you the choice of a product that is warranted for five years versus one that is warranted for ten years – and the price for the longer warranty is within reason, it may be more valuable to choose the product with the longer warranty. It may cost more initially but it is less likely to be serviced as much and will last longer.

Similarly, your contractor may offer a value proposition which includes a “good,” “better,” “best” scenario for the product you are shopping for. You may choose from any of the three based on the amount of time you plan to live in your home or the level of comfort or convenience that you are accustomed to. And, if you choose a “good” product over a “best” product, it may diminish the value of your house when it comes time to sell.

Any good contractor who gives you these choices is one who is giving you the best value.

When it comes to service, there are also value choices, too. For example, how important is it to you to work with a contractor who values your time? Today, time can be just as important as money and is certainly a value consideration. One contractor may only be able to give you a large window of time when his company will be able to serve you, say 8:00 a.m. to 3:00 p.m. Is it worth your time or someone else’s to wait?  It may cost a little more but is it worth it to you? The answer is likely to be yes; and this adds a value to the contractor who respects your time.

The true value of a contractor lies in the equipment he sells, the service he provides, and the peace-of-mind and time savings you get in return.

Continue Reading

How Do I Check a Gas Furnace Draft Pressure Switch? A Question From Kent

Wednesday, September 28th, 2011

Since Fall has started, it important to be prepared for the upcoming winter in Kent. It is a good idea to get yourself ready by learning some basic information about your home’s heating system. For instance, there are many reasons why a gas furnace stops working and in many cases, a homeowner can perform some simple diagnostics to pinpoint the problem. Finding the problem is one thing – fixing it is another. When in doubt, don’t try it yourself. Call a qualified professional.

But let’s look at one possible problem and solution you may be able to perform yourself – testing the draft pressure switch. The draft pressure switch on a gas furnace allows an electrical current to pass through to ignite the furnace. The pressure switch monitors the draft conditions and won’t allow the furnace’s gas valve to open unless draft is correct.

If the switch is malfunctioning, so too will (or will not) the furnace.

The best way to locate the switch is by consulting with your owner’s manual or by going online and simply typing in the words “gas furnace draft switch.” It is identifiable by its round size and is bolted to the outside of the furnace. It should be nearby the draft inducer motor because the two are connected by a metal tube. The tube may sometimes be the culprit, too. A tube that is blocked with condensation may cause the switch to go bad.

To check for proper function, first turn off power to the furnace, either by shutting down the “on’ switch at the furnace or shutting off the circuit breaker.

Use a volt ohm meter to check if the switch is opening and closing properly. Start by zeroing out the meter’s probes by touching the tips together. Using the dial (could be analog or digital), set the meter to 24 volts. Ground the black probe by attaching it to any metal part of the furnace. Then place the end of the red probe on the metal tube connecting the draft pressure switch to the draft inducer motor.

If the switch is working properly the meter should read at least 24 volts, or very near that. If the reading is short of 24 volts, the switch is not working correctly. At that point you may decide to replace it or call a professional to do the task (recommended).

Always remember that there are many sources which will help you diagnose and repair a problem, especially those available through the Internet. If you search YouTube.com you will find many videos advising you on how to repair certain components. Use all of the resources available to you and keep the phone number of a qualified and professional heating and cooling contractor nearby.

Continue Reading

Window and Through Wall Units – Benefits and Disadvantages in Kent

Wednesday, August 10th, 2011

When you’re trying to decide what type of air conditioner to get for your Kent home, you’ll first have to determine whether a central air conditioning system or smaller individual unit is best for you. These smaller air conditioners are generally installed either in a window or through the wall of your home, and they can provide excellent cooling under the proper conditions.

If you’re still on the fence about what type of air conditioner is right for your home, here are a few items to consider:

  • Ducts – If your home already has ductwork installed for a central forced air heating system, it should be relatively easy to hook up a central air conditioner. But if there are no ducts currently in place, your installation costs will be a lot lower with window or wall mounted units.
  • Portability – Most window units are designed to be removed and stored at the end of the summer, so you can have your windows back and not have to look at that unit all winter long. Through wall units aren’t generally removable, but because they don’t take up window space and provide a more thorough seal against the elements, that’s not as much of a concern.
  • Aesthetics – With both window and through wall units, you’ll have something protruding into your room at least a few inches. These types of units are hard to hide, particularly when compared to the simple air ducts that central air conditioning systems use.
  • Flexible Sizing – No matter how big or small your room is, you should have no trouble finding a window or through wall unit to match it. A central air conditioning system needs to be sized to fit the entire house. If you’re only inclined to use air conditioning in two or three rooms during the hottest months of the year, you may not want to pay to cool the entire house all of the time. Smaller units provide that type of flexibility.
  • Affordability – Installing a central air conditioning system, even if you already have ducts in place, is a large undertaking and likely to cost you several thousand dollars up front. On the other hand, small window and through wall air conditioners are available for as little as $200 and you can buy more whenever you’re ready to spend that extra money. You can also usually install a window unit yourself, and the cost of having a through wall unit installed is minimal compared to that of a central AC unit.

Continue Reading

Allergens: Regular Duct Cleaning Will Reduce Them

Friday, June 3rd, 2011

One of the biggest problems many families face with indoor air quality is the ever persistent presence of allergens. Especially if you have pets or plants, allergens will be in your home from the day you move in. But, that doesn’t mean there aren’t many ways to reduce them – especially in the case of duct work.

Allergens in Your Duct Work

How do so many allergens get into your ductwork? It starts with how the ductwork circulates air in your home. Because air only flows one way and because the ducts are not being used continuously, the air circulated by your air conditioner or furnace leaves behind all sorts of unwanted residue.

In both cases, the air drawn into your comfort system is usually the same air from inside your home. That means it is full of things like dust, pollen, dander and more. Even if the air is drawn from outside, often the case with an air conditioner unit, there are plenty of allergens outside.

How do you stop all of these allergens from working their way into your home and then your lungs? It starts with regular cleaning. You can’t ever truly stop allergens from coming inside or circulating in your air ducts, but you can take big steps in removing many of the contaminants that linger in your ducts.

Annual cleaning of the ducts by a professional will remove excess build up in places you cannot normally reach. Between those cleaning visits, you should supplement the cleaning by dusting and vacuuming vents and the areas of your ducts you can reach.

Going Beyond Cleaning

Cleaning your ducts is a great way to reduce allergens in the house. That alone, along with quality ventilation will take care of the most common allergens. However, if people in your home suffer from asthma or more severe seasonal allergies you may want to upgrade your preventative measures with an air filtration and purification system.

An air filter alone, equipped with a HEPA filter, is capable of removing particles and allergens as small as 0.3 microns – far smaller than dander, pollen or dust. For those with more advanced allergies or too many outdoor contaminants, a purifier works wonders by removing excess gas, smoke, or mold from the air with ionization.

Whatever your concerns, it is possible to live comfortably in your home despite allergies. Stay on top of cleaning and get your air tested to see if filtration will help. From there, you can remove almost anything.

Continue Reading

How to Judge the Quality of a Ceiling Fan

Monday, May 2nd, 2011

Like just about anything else on the market these days, there are good ceiling fans and there are low quality ones. With such a seemingly simple piece of equipment, it can be tempting to just grab the cheapest one you can find. After all, how much of a difference can it really make? In fact, the quality of the ceiling fan you buy can have a significant impact on its performance level and how long it lasts.

Of course, you do not necessarily want to go out and buy the most expensive thing you can find either. There are many good quality ceiling fans that will not cost you an arm and a leg, but you need to know how to find them and separate them from the rest of the pack.

One of the first things to look for when you are evaluating your ceiling fan options is how much of an angle the blades have. This angle usually ranges from eight to 15 degrees and the bigger the angle, the more air the fan can move at once.

However, cheaper fans with a less powerful motor cannot handle the resistance that a higher volume of air generates. What that usually means is that the units with the smaller blade angle are less powerful and will be less effective at circulating air throughout your room. Even when they are running at the same speeds, the blades with the smaller angle will move less air, and so they will not keep you as cool.

You should also check the various ceiling fans you are considering to make sure they are the right size to fit your room. To be safe, a ceiling fan’s blades should be no less than seven feet above the floor. But if you have very high ceilings, you may want to add something that can extend the fan down closer to the floor so that you will still feel all of the cooling effects it produces.

The various ceiling fans on the market right now all have many different features that can influence your decision as well. For instance, you may want to opt for a fan that has programmable settings or that comes with a remote control for more convenient access. But if these are not features you care about, you can probably save quite a bit by going with a no-frills model.

Continue Reading